Differential temp and antifreeze system
#1
Hi.
I have two temp sensors. I configure without problem the differential part and everything works ok. When the difference is above 4 degrees Celsius the Relay is changing state (pump is on), else the relay is open (pump is off).
I want to configure also the 7 input (temperature sensor) for antifreeze. When the Temperature is 1 Degree Celsius the Relay must change state (pump on), else the relay is off (pump off).

Can I do that and how? Please help.
Christos
<t></t>
Odpowiedz
#2
add print screen from your events config
pozdrawiam
tomek
Odpowiedz
#3
Photos uploaded. Thank you


.png   tiny01.png (Rozmiar: 64.51 KB / Pobrań: 2,451)


.png   tiny02.png (Rozmiar: 34.33 KB / Pobrań: 2,444)

The differential is OK bt I want the antifreeze in the same time for temperatures below 1 degree Celsius (the pump must be on).
<t></t>
Odpowiedz
#4
I think I managed to configure the antifreeze.
In Inp7 I put -20.0 and 3.0