Hi.
I have two temp sensors. I configure without problem the differential part and everything works ok. When the difference is above 4 degrees Celsius the Relay is changing state (pump is on), else the relay is open (pump is off).
I want to configure also the 7 input (temperature sensor) for antifreeze. When the Temperature is 1 Degree Celsius the Relay must change state (pump on), else the relay is off (pump off).

Can I do that and how? Please help.
Christos
add print screen from your events config
Photos uploaded. Thank you

[attachment=369]

[attachment=370]

The differential is OK bt I want the antifreeze in the same time for temperatures below 1 degree Celsius (the pump must be on).
I think I managed to configure the antifreeze.
In Inp7 I put -20.0 and 3.0