Forum Tiny Control Solution
Differential temp and antifreeze system - Wersja do druku

+- Forum Tiny Control Solution (https://forum.tinycontrol.pl)
+-- Dział: LanKontroler - sprzęt i wersje wsadów, problemy, zastosowanie (https://forum.tinycontrol.pl/forumdisplay.php?fid=3)
+--- Dział: LanKontroler - wersje oprogramowania (https://forum.tinycontrol.pl/forumdisplay.php?fid=4)
+---- Dział: Przykłady zastosowań przez użytkowników. (https://forum.tinycontrol.pl/forumdisplay.php?fid=6)
+---- Wątek: Differential temp and antifreeze system (/showthread.php?tid=649)



Differential temp and antifreeze system - pras - 11-02-2015

Hi.
I have two temp sensors. I configure without problem the differential part and everything works ok. When the difference is above 4 degrees Celsius the Relay is changing state (pump is on), else the relay is open (pump is off).
I want to configure also the 7 input (temperature sensor) for antifreeze. When the Temperature is 1 Degree Celsius the Relay must change state (pump on), else the relay is off (pump off).

Can I do that and how? Please help.
Christos


Re: Differential temp and antifreeze system - wilkxt - 11-03-2015

add print screen from your events config


Re: Differential temp and antifreeze system - pras - 11-04-2015

Photos uploaded. Thank you


.png   tiny01.png (Rozmiar: 64.51 KB / Pobrań: 2,446)


.png   tiny02.png (Rozmiar: 34.33 KB / Pobrań: 2,441)

The differential is OK bt I want the antifreeze in the same time for temperatures below 1 degree Celsius (the pump must be on).


Re: Differential temp and antifreeze system - pras - 11-05-2015

I think I managed to configure the antifreeze.
In Inp7 I put -20.0 and 3.0