Possible upgrades events
#11
kollnjak post_id=10762 time=1497215645 user_id=5763 napisał(a):Thank you for your advice, I'll see you all ..

I have another question, do you manually turn ON/OFF virtual outputs (EVNT1-EVNT8) ??
No, only by event
pozdrawiam
tomek
Odpowiedz
#12
Hi,

1) I have encountered an error in the event, see picture (DS4=72°C, but DS4 same condition, other behavior LK3) ..
The separate condition works correctly, but with DIFF is not correct

.jpg   chyba teploty.jpg (Rozmiar: 65.44 KB / Pobrań: 1,868)

2) would the ON / OFF outputs of the event page be displayed (GREEN/RED)?
3) would you see virtual outputs ON / OFF on page control / output?
<t></t>
Odpowiedz
#13
I will check this in next week
pozdrawiam
tomek
Odpowiedz
#14
Hello,

Is this train still alive? Has it ever been resolved?

Thank you in advance for your good work
<t></t>
Odpowiedz
#15
check this soft http://tinycontrol.pl/forum/download/file.php?id=550
pozdrawiam
tomek
Odpowiedz
#16
Hi,

Upgraded firmware on 1_39b1, but i do not see changes .. viz obrazek


.jpg   LK3-mistake.jpg (Rozmiar: 170 KB / Pobrań: 1,830)

1) bad condition prediction, see blue circle image (top blue circle is right with output OUT3)

2) will display output status (yellow circle) ON / OFF - Green / Red

3) DIFF1,2 and ENT1-EVNT8 - virtual outputs do not manually switch on/off or display ("status page", "control/out page")

Thx your jobSmile

Kollnjak
<t></t>
Odpowiedz
#17
what is value diff1 and DS4?
pozdrawiam
tomek
Odpowiedz
#18
I think there is a problem in temperatures in the second part of the condition, see the next picture


.jpg   LK3-mistake2.jpg (Rozmiar: 132 KB / Pobrań: 1,818)

The first(top) oranges circle is the correct (DS3=25°C, OUT1=OFF)
<t></t>
Odpowiedz