08-05-2022, 07:31 AM
(08-04-2022, 08:40 PM)tomas.hofman napisał(a): I am testing after a factory reset.
Test result
Reset to factory settings
The PC is connected only with a tinycontrol network cable, there is no connectivity to the Internet or other technologies.
the ping responded to the address 192.168.1.100
We logged in at the same time as the ping.
HTTP://192.168.1.100
files ping-4-192-168-1-100.txt and putty-tinycontrol-com3-v4-192-168-1-100.txt are from the beginning of the reset
tinycontrol worked with this setting for 2 hours without any problems.
Set required ip 172.16.32.124
The PC is connected only with a tinycontrol network cable, there is no connectivity to the Internet or other technologies.
ping responded to 172.16.32.124
We logged in at the same time as the ping.
HTTP://172.16.32.124
The files ping-5-172-16-32-124.txt and putty-tinycontrol-com3-v5-172-16-32-124.txt are from the start with the new IP address
tinycontrol worked with this setting for 7 hours without any problems.
In the afternoon I will perform tests with the Internet connection and report back.
Thank you for your help, whether the problem is solved.
Greetings Tom