wilkxt napisał(a):Nothing happend because config events switches outs when the signal exceeds the setpoint + hysteresis and next setpoint- hysteresis.
In this case you have set point 17+ 0,6 hysteresis, if temp was below 17-0,6 (=17,6, then out0 OFF.
But if temp was above 16,4 (eg. 16,8) and next go to >=17,6, nothing hapend because temp never was below 16,4.
See picture
[ATTACHMENT NOT FOUND]
ok, when I push on by scheduler, I must stop by scheduler (for sure), I understand
It works well for other purposes.
New question:
Are you thinking about trigger which stop(start) the output depending on actual temperature, not hysteresis?
Thank you a lot for your time.