08-04-2017, 08:47 AM
For v2 i used `ind.cgi?kw2=1`. How do i proceed for v3?
Thanks
Thanks
How to enables the counting of pulses for V3 controllers
|
08-04-2017, 08:47 AM
For v2 i used `ind.cgi?kw2=1`. How do i proceed for v3?
Thanks
08-04-2017, 02:44 PM
In the power tab, you have to select one of the INPDs as the input.
To to this by command http GET use: inpa.cgi?powsel=06 for INPD1 in E1 inpa.cgi?powsel=07 for INPD2 in E1 inpa.cgi?powsel=08 for INDP3 in E1 inpa.cgi?powsel=09 for INDP4 in E1 inpa.cgi?powsel=16 for INPD1 in E2 inpa.cgi?powsel=17 for INPD2 in E2 inpa.cgi?powsel=18 for INPD3 in E2 inpa.cgi?powsel=19 for INPD4 in E2 inpa.cgi?powsel=26 for INPD1 in E3 inpa.cgi?powsel=27 for INPD2 in E3 .......etc.
pozdrawiam
tomek |