07-09-2024, 03:37 PM (Ten post był ostatnio modyfikowany: 07-22-2024, 01:52 PM przez dusanstr.)
Hello, I want to ask you for help.
Via LK3, I load data from the BMS Li-ion battery via Modbus in the user settings. Everything works perfectly, I just have a problem with the display of the negative current when discharging the battery, it displays the positive value correctly.
Well thank you
Solar panels: 3960 Wp, Solar Controller: EPEVER-150VDC/80A, Inverters: Household / Victron 5000 VA/24V, Water heating / Victron 3000 VA/24V, Li-ion battery: 18650 56P/8S + Li-ion 50Ah 3P/8S + Li -ion 150Ah 8S = 31.6V/440Ah (LK3, LK3.6, LK3.8)
Does anyone here use communication between LK3 and BMS of the accumulator via modbus?
Can anyone advise how to set LK3 so that it also correctly displays the minus value of the current?
Well thank you
Solar panels: 3960 Wp, Solar Controller: EPEVER-150VDC/80A, Inverters: Household / Victron 5000 VA/24V, Water heating / Victron 3000 VA/24V, Li-ion battery: 18650 56P/8S + Li-ion 50Ah 3P/8S + Li -ion 150Ah 8S = 31.6V/440Ah (LK3, LK3.6, LK3.8)
(07-22-2024, 01:52 PM)dusanstr napisał(a): Does anyone here use communication between LK3 and BMS of the accumulator via modbus?
Can anyone advise how to set LK3 so that it also correctly displays the minus value of the current?
Well thank you
wykryto błąd w odczycie wartości ujemnej na ModBusie... prawdopodobnie soft ją obrabia i zwraca modulo
e-chata.hyzne.com | LK1 - sterowniki akwarystyki | LK2 - sterowniki ihome | LK3 - niezliczone ilości wersji/nakładek na farmach PV i nie tylko | LK4 - testy bezprzewodowe
(07-09-2024, 03:37 PM)dusanstr napisał(a): Hello, I want to ask you for help.
Via LK3, I load data from the BMS Li-ion battery via Modbus in the user settings. Everything works perfectly, I just have a problem with the display of the negative current when discharging the battery, it displays the positive value correctly.
Check if the current value from the BMS is a signed integer and configure the LK3 to interpret it as such. Verify Modbus register settings and scaling factors in LK3. Use a Modbus diagnostic tool to confirm raw data, and update firmware if needed. Contact LK3 support if the issue persists.
Thanks for the answer.
I don't understand how to verify this " Check if the current value from the BMS is a signed integer and configure the LK3 to interpret it as such. Verify Modbus register settings and scaling factors in LK3. Use a Modbus diagnostic tool to confirm raw data "
My firmware is up to date, I have contacted LK3 support several times, but I haven't received any response.
Have a nice day.
Solar panels: 3960 Wp, Solar Controller: EPEVER-150VDC/80A, Inverters: Household / Victron 5000 VA/24V, Water heating / Victron 3000 VA/24V, Li-ion battery: 18650 56P/8S + Li-ion 50Ah 3P/8S + Li -ion 150Ah 8S = 31.6V/440Ah (LK3, LK3.6, LK3.8)
Check if your LK3 is reading the current as unsigned; changing it to signed (INT16) should display negative values correctly. Some BMS systems also use a separate register to indicate charge or discharge mode. If so, you may need to manually adjust the sign based on that register. Baldi’s Basics Plus
(07-09-2024, 03:37 PM)dusanstr napisał(a): Hello, I want to ask you for help.
Via LK3, I load data from the BMS Li-ion battery via Modbus in the user settings. Everything works perfectly, I just have a problem with the display of the negative current when discharging the battery, it displays the positive value correctly.
Well thank you
I can confirm that negative reading via MODBUS is now working in the new SW 1.65 version.
Thank you
Solar panels: 3960 Wp, Solar Controller: EPEVER-150VDC/80A, Inverters: Household / Victron 5000 VA/24V, Water heating / Victron 3000 VA/24V, Li-ion battery: 18650 56P/8S + Li-ion 50Ah 3P/8S + Li -ion 150Ah 8S = 31.6V/440Ah (LK3, LK3.6, LK3.8)